Good morning,
I found a problem in a simple configuration. In the attachment, there is a file (separate system) in which there are 2 different loops of 2 different fluid. This configuration works without any problems.
Then I try to insert an external heat exchanger between the 2 loops and the following problem arise:
"" The circuit: "Transfer circuit" contains several flow producers. ""
How can I simulate this simple heat exchange between these 2 fluids?
Thanks for the support.
Mass flow rate error (external heat exchanger) Thema ist als GELÖST markiert
-
- Beiträge: 66
- Registriert: Mo Jun 18, 2018 4:01 pm
Good morning TurCoim
You have to get rid off one of two the pumps in the loop.
Sunny greetings
Nathanael
You have to get rid off one of two the pumps in the loop.
Sunny greetings
Nathanael
Good morning Nathanael,
the two loops contain different fluids and so I inserted two different pumps because there are two different flow rates. I would simply like to simulate a thermal change between these two different loops and therefore I want to simulate them by interposing an external heat exchanger, such as the plate heat exchanger.
How can I communicate to the software a variable and unknown thermal exchange, as the mass flow rates and temperatures vary, trying to make the software understand that the loops are different, without running into this problem?
Thanks a lot for the support.
Best regards
TurCoim
the two loops contain different fluids and so I inserted two different pumps because there are two different flow rates. I would simply like to simulate a thermal change between these two different loops and therefore I want to simulate them by interposing an external heat exchanger, such as the plate heat exchanger.
How can I communicate to the software a variable and unknown thermal exchange, as the mass flow rates and temperatures vary, trying to make the software understand that the loops are different, without running into this problem?
Thanks a lot for the support.
Best regards
TurCoim
Good morning,
The aim of the project is to insert an external plate heat exchanger (no mixing) and exchange heat from the solar fluid loop with an organic fluid under pressure (therefore in a liquid state) in another loop as in the figure.
It would, therefore, be a heat exchange in an external heat exchanger (plate type) between two different fluids, with of course two different mass flow rates.
I am sorry for the series of questions I am asking you, but I thank you very much for the speed and quality of the answers. Having solved this last doubt I believe I can carry out the series of simulations as designed in my project.
Looking forward to your reply, I wish you a good day
The aim of the project is to insert an external plate heat exchanger (no mixing) and exchange heat from the solar fluid loop with an organic fluid under pressure (therefore in a liquid state) in another loop as in the figure.
It would, therefore, be a heat exchange in an external heat exchanger (plate type) between two different fluids, with of course two different mass flow rates.
I am sorry for the series of questions I am asking you, but I thank you very much for the speed and quality of the answers. Having solved this last doubt I believe I can carry out the series of simulations as designed in my project.
Looking forward to your reply, I wish you a good day
-
- Beiträge: 66
- Registriert: Mo Jun 18, 2018 4:01 pm
Ok, in that case you need to reconfigure the heat exchanger.
Right know you have one loop. By changing the tubes like in the picture, you can divide the loop into two loops.
Sunnny greetings
Right know you have one loop. By changing the tubes like in the picture, you can divide the loop into two loops.
Sunnny greetings