Seite 1 von 1

Priority order for multiple heat generators.

Verfasst: Mo Nov 20, 2017 3:48 pm
von Zaideus
I am unable to find the right control, which can enable me to set priority order for a system with multiple heat generators. In absence of a prrority control, the generators are starting at the same time, resulting in very large surplus energy.
Thanks,
AZ

Re: Priority order for multiple heat generators.  Thema ist als GELÖST markiert

Verfasst: Di Nov 21, 2017 12:01 pm
von Lars Kunath
Dear AZ,
the control strategy you can easily change by using either different sensor positions or different temperatures for the controller.
E.g. you have a heat pump (first priority) and an electrical heater (second priority). Just switch on the heat pump as soon as the temperature in the storage tank is below 50 °C and switch it off as soon it is above 55 °C. For the electrical heater use switch on temperature 45 °C and switch off 50 °C
-> in this case the electrical heater will just run when the heat pump cannot deliver enough energy (temperature will go down)

Hope this helps!

BR Lars